Guyz, what is the usually cause nga magoverload ang ups? Mao ni ako problema sa ako ups ron..
Guyz, what is the usually cause nga magoverload ang ups? Mao ni ako problema sa ako ups ron..
pila man na VA ang UPS mo?
bacin 500 VA ra na unya ang PC specs mo taas kaau mokaon og kuryente.
ill check on it..
Pero i've been using this for almost 8 months and karon ra jd ni na overload. Wala mn koy lain g.connect sa UPS ang System Unit ra ug ang Monitor.
yes basin overload gyud.
500VA UPS has a maximum load of only 300Watts.
UPS 500VA = 300 Watts How come?? Please??
Because current is delayed compared to voltage. As I mentioned in a similar thread, look at the wattage instead of the VA ratings.
Things to watch on UPS: wattage, voltage regulation, signal type (Pure Sine & Adaptive Sine > Step Wave), back-up time-limit, and other features (some have software that automatically changes the PCs power settings and eventually shut it down at set time when there is no power feeding the UPS).
Note that the signal type is important because if you have a step wave (cheapest) and you are in the zero state when the power if cut (brownout), the UPS will not activate.
Last edited by P0w3rM0v3; 05-26-2011 at 08:24 AM.